Ask Your Question
0

Error: Messages for api DIST_SPCB_FAULT_2

asked 2017-08-21 13:43:41 -0500

When try to perform "calculate and apply branch unbalance" from dynamic tap the following message appear:

Messages for api DISTSPCBFAULT_2 No sequence data in memory (004290)

Can anyone help me with this error? I'm Using V.33.4

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2017-08-21 15:59:42 -0500

perolofl gravatar image

Your saved case does not contain sequence data so you cannot use DISTSPCBFAULT_2.

Use instead DISTBRANCHFAULT to simulate a balanced line fault.

edit flag offensive delete link more

Comments

Thanks perolofl, may i ask if you have any IEEE network (14,30, 39,...etc) contains sequence data?

Amr gravatar imageAmr ( 2017-08-25 22:01:49 -0500 )edit

I have this problem too. Have you solved it?

AlexYang gravatar imageAlexYang ( 2018-05-16 01:56:04 -0500 )edit