Ask Your Question
0

Pelec calculation based on Efd

asked 2017-03-03 14:38:22 -0500

eve gravatar image

Hi folk,

Anyone knows what is the reference voltage for the exciter field voltage Efd? I'm trying to calculate Pelec two different ways but either of them can match the Pelec given by PSS/E. So I wonder if the Efd and Vbus are in different reference settings. Or there are some other reasons for this?
I provided the process for the calculation below: (Noted: All the angles are in absolute values)

1.

Pelec = EfdVbussin(rotor angle)/Xs.

2.

Pelec =real{ Efd*[cos(rotor angle) + jsin(rotor angle)] * conj (I)}

where

I = {Efd[cos(rotor angle) + jsin(rotor angle)] - Vbus[cos(bus angle) + jsin(bus angle)]} / jXs

Thank you , Eve. :)

edit retag flag offensive close merge delete

1 answer

Sort by » oldest newest most voted
0

answered 2017-03-04 05:53:59 -0500

ffl gravatar image

Did you try to use Eterm instead?

edit flag offensive delete link more

Comments

Hi, Eterm is actually Vbus but I need internal field voltage which is Efd in PSS/E.

eve gravatar imageeve ( 2017-03-08 01:35:09 -0500 )edit

My mistake, yes I agree. Is this a flat run simulation?

ffl gravatar imageffl ( 2017-03-10 05:30:02 -0500 )edit

Hi, Eve, I also tried to calculate Pe based on your equation. Did you find out the way to calculate the correct PELEC ?

dunguyen9003 gravatar imagedunguyen9003 ( 2020-07-22 22:10:15 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2017-03-03 14:38:22 -0500

Seen: 679 times

Last updated: Mar 04 '17