PSSE Exciter Step response test
Hello, all
The default psse exciter step response is done by changing reference from 1 to 1.1 pu Can anyone to suggest me to do exciter step response from 0.5 to 0.55 pu
Thank you
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Hello, all
The default psse exciter step response is done by changing reference from 1 to 1.1 pu Can anyone to suggest me to do exciter step response from 0.5 to 0.55 pu
Thank you
Generator normal operating voltage is around 1.0 pu. What conditions are you testing with "exciter step response from 0.5 to 0.55 [V] pu"?
The API for this activity allows setting the step change (estr_open_circuit_test
).