Generator Modulation During Dynamic Simulation

asked Sep 29 '15

Lassettc gravatar image

Is there a way to change a generator's power output during dynamic simulation? I'd like to create a pilot signal, as in a pulse, and embed it in a generator and observe changes in the system during dynamic simulation.

Thanks

3 answers

Sort by » oldest newest most voted
0

answered Oct 11 '16

perolofl gravatar image

The easiest way to modulate the power of a fictive generator is to represent it with a negative load and change the load value during the simulation. You will then see how a pure power pulse affects the rest of the system.

link

Comments

How to modulate (sine function?) the P and Q of the negative load?

jconto gravatar imagejconto (Oct 12 '16)

A sine function is of course more difficult. For that you need to write a user model that updates the load every time step.

perolofl gravatar imageperolofl (Oct 12 '16)
0

answered Oct 3 '15

Jacde gravatar image

If you don't want to create a user defined model, a python-based hybrid simulation such as a phase shifter in front of an infinite gen could work.

link
0

answered Sep 29 '15

jconto gravatar image

A user-defined exciter model (in fortran) could control the terminal voltage of a classic-model generator in a single-machine infinite-bus setup. This SMIB simulates the network equivalent connected to the device under test. At every time step, this exciter's Voutput will follow the signal generator function in time. Any takers?

link

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.
Want to format code in your answer? Here is a one minute demo on Youtube