Exciter fault
Can I simulate generator exciter fault in dynamic analysis?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Can I simulate generator exciter fault in dynamic analysis?
Loss of excitation may be simulated by forcing Efd to 0 by changing field voltage maximum and minimum voltage with API changeplmodcon:
psspy.change_plmod_con(211,'1','SCRX',5,0.0)
psspy.change_plmod_con(211,'1','SCRX',6,0.0)
In this simulation EFD is set to zero at time=1 s.
Asked: 2015-07-30 09:05:13 -0500
Seen: 549 times
Last updated: Oct 11 '16
How to ramp the value of exciter output voltage in dynamic simulation?
Applying a SLG fault with delayed clearing
Issue Running Dynamic Simulation in Loop, PSSEv35 vs PSSEv34
IEEE system bus data with sequence data for unbalanced fault
Voltage Spike after deep fault
Count the number of network not converged message
Network does not converge due to large amount of CLMDBLU2 in system