Ask Your Question
2

Loadflow: Power factor in a remote bus

asked 2015-02-04 22:34:33 -0600

google gravatar image

Hi,

In PSS/E v32, is there a way of using a machine to remotely control the power factor in a given bus?

I think that voltage can be controlled in this way, but it seems to me that PF can only be controlled locally.

Thanks

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2022-06-29 12:02:56 -0600

Basically, the machine is connected to a generator bus(PV). you have control over P and V.

In steady-state model, if you want to set the power factor at a bus, you can force the reactive power to +ve for lagging and -ve for leading according to the required power factor.

Another way is by changing the Scheduled voltage of the generator to get the desired power factor at the remote bus.

But in dynamics, you can operate a generator/plant in power factor control using the power plant controller(PPC) model.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

Stats

Asked: 2015-02-04 22:34:33 -0600

Seen: 1,192 times

Last updated: Jun 29 '22