Regulation of remote bus - any limitations of PSS/e?

asked 2025-07-18 16:39:05 -0500

_____ja gravatar image

updated 2025-07-21 01:18:20 -0500

perolofl gravatar image

I'm trying to understand better PSS/e and I wonder are there any limitations related to definition of regulation

a) case a. for example is it problematic for PSS/e to handler regulation of the same bus with two generators connected directly to the same bus (implicit modeling approach)?

b) case b. Generator is connected through step up transformer equipped with tap changer (explicit modeling approach) indication both the same remote bus of station B.

c) are there any other limitations that you have encountered while modeling (related to indicated bus for regulation)?

d) do you practice to simplify modeling for some reason and point to different place then in reality?

e) is there any limitation how far remote bus can be?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2025-07-21 01:17:10 -0500

perolofl gravatar image

a) All generators connected to a bus use the same Plant data, i.e. same voltage setpoint.

b) Assign same Vsched to both generators. PSSE will use Vsched of the first generator if Vsched are not the same.

e) The remote bus should be electrically nearby. If not, there will be transfer of reactive power and voltage drops in the network.

The best is to test by yourself and see the result.