Ask Your Question
0

Amps in Node-Breaker Analysis

asked 2025-06-09 11:55:19 -0500

bdeanna gravatar image

Hello,

I am trying to find the equivalent amps through the breakers for a substation with node-breaker analysis. Is there any option to display amps in the node-breaker diagram or output a report in PSSE to display the amps through the breakers?

Thank you in advance.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2025-06-09 14:51:05 -0500

perolofl gravatar image

updated 2025-06-10 02:24:26 -0500

In a diagram:

Select Diagram - Properties and Amps in Load Flow Annotation.

EDIT:

Here is a node-breaker diagram for bus 153 in savnw:

image description

AMPS/PU Current is shown here.

edit flag offensive delete link more

Comments

Hi Unfortunately that does not show the amps going through a specific breaker in the nodebreaker diagram. That only displays the amps for the external branches of the substation bus node diagram. I am looking for the a way to see the amps going through each individual breaker in the substation model

bdeanna gravatar imagebdeanna ( 2025-06-09 15:30:40 -0500 )edit

It works for me!

perolofl gravatar imageperolofl ( 2025-06-10 02:26:22 -0500 )edit