Generator trip by out of step
Hello,
What is the tool in PSSE which trips the generator in case the generator is subjected to a rotor angle instability? How to implement it?
Thanks in advance for all of you.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Hello,
What is the tool in PSSE which trips the generator in case the generator is subjected to a rotor angle instability? How to implement it?
Thanks in advance for all of you.
Dynamic Simulation Options - Generic Scan - Scan generators exceeding angle threshold.
Select a proper angle for trip and "Monitor and trip".
Thank you so much. It succeeded. I have PSSE Ver. 33.4 The options available were checking Scan for generators exceeding angle threshold I selected Angle Threshold 180 & MBASE threshold. So if needed now to trip by under frequency? I have to add ’FRQDCAT’ to my DYR file or other solution?