Generator trip by out of step
Hello,
What is the tool in PSSE which trips the generator in case the generator is subjected to a rotor angle instability? How to implement it?
Thanks in advance for all of you.
Hello,
What is the tool in PSSE which trips the generator in case the generator is subjected to a rotor angle instability? How to implement it?
Thanks in advance for all of you.
Dynamic Simulation Options - Generic Scan - Scan generators exceeding angle threshold.
Select a proper angle for trip and "Monitor and trip".
Thank you so much. It succeeded. I have PSSE Ver. 33.4 The options available were checking Scan for generators exceeding angle threshold I selected Angle Threshold 180 & MBASE threshold. So if needed now to trip by under frequency? I have to add ’FRQDCAT’ to my DYR file or other solution?