Ask Your Question
0

PLBVFU1 Frequency Ride Through Testing

asked Mar 1 '5

Engineer Power System gravatar image

updated Mar 1 '5

perolofl gravatar image

I am trying to test frequency ride through in PSSE for 0.3Hz step/down from 60 Hz. My PLBVFU1 model looks like

"260 'USRMDL' 1 'PLBVFU1' 1  1  3  4  3  6  1  1 'BA3_Play_RT' 1.0 60.0 0.00 0.00 /"

in dyr file, also my plb file is

@!time, V(kV), f(Hz) 
@!6.5 TO 6.8 FAULT
0.0         1.0     60.0
6.5         1.0     60.0
6.5001      1.0     60.3
6.8         1.0     60.3
6.8001      1.0     60.3    
12.0        1.0     60.0.

When I plot them in PSSE, I don't see frequency from 60 Hz to 60.3 Hz, instead plot starts from 1 goes to 0.005 and back to 1.

Can anyone help is finding the issue, also how can I plot 60 Hz data in PSSE. Am testing these models against PSCAD where frequency is in 60 Hz. Because of this difference, I can't plot both the PSSE and PSCAD values on same plot for MQT's.

1 answer

Sort by » oldest newest most voted
0

answered Mar 1 '5

perolofl gravatar image

PSSE doesn't plot the frequency in Hz, it shows instead the per unit speed deviation. This means that 60 Hz is 0 pu speed deviation and 0.005 pu = (1+0.005)60 = 60.3 Hz.

There are many posts here describing this, for example: Frequency zero

link

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.
Want to format code in your answer? Here is a one minute demo on Youtube

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: Mar 1 '5

Seen: 91 times

Last updated: Mar 01