PMECH Initialized out of limit: PMECH (pu on Trate)= 0.7727 Flow (q) Initialized out of limit: Flow= 0.8667

asked 2024-09-25 00:54:02 -0500

junaid2657@gmail.com gravatar image

I am getting this messages on my multiple machine while initializing dynamic simulation. What could be the possible error?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2024-09-25 05:00:57 -0500

perolofl gravatar image

Pgen in load flow is higher than the limit in the governor model. Reduce Pgen in load flow or increase the limit in the governor model.

edit flag offensive delete link more

Comments

I have received the governor model from the O&M. And also the Pgen values, would it be recommended to change those limits?

junaid2657@gmail.com gravatar imagejunaid2657@gmail.com ( 2024-09-26 00:47:38 -0500 )edit

Increase the limit in the governor model.

perolofl gravatar imageperolofl ( 2024-09-26 01:55:25 -0500 )edit

Yes, it worked. the message has disappeared thanks.

junaid2657@gmail.com gravatar imagejunaid2657@gmail.com ( 2024-09-27 06:02:53 -0500 )edit

Model GGOV1 Bus xxxx [xxxx-4 GT 18.500] Machine "1 " : initialized out of limit(s) V3 can you tell me what is V3 here?

junaid2657@gmail.com gravatar imagejunaid2657@gmail.com ( 2024-09-27 06:40:07 -0500 )edit

I believe it is a typo. Maybe they mean S3 for STATE(K+3)?

perolofl gravatar imageperolofl ( 2024-09-28 01:47:58 -0500 )edit