Ask Your Question
0

I want to suddenly change wind generator's reactive power during dynamic simulation. Please help.

asked 2024-07-11 17:50:01 -0600

Stokes CB gravatar image

updated 2024-07-13 11:59:21 -0600

I am working on the 14 bus system and replaced one of the generators with a wind machine 'Standard QT QB limits' and set WPF to 0.95. The dynamic models used are REGCA1, REECB1 and REPCA1. In the raw data, I have provided enough provision (through Qmax Qmin limits) for reactive power to change at least slightly upon issuing commands from control models. I have been attempting to cause a step response in reactive power production but unable to. For this, I have made sure to assign Qflags or Qcontrol mode and trying to change Vref VARS at REECB1 and REPCA1. I also attempted changing Qref, Pref but cannot see a change in power output plots. Please advise.

Dynamic data sample:

6533 'REGCA1' W 1 0.20000E-01 10.000 0.90000 0.40000 1.2200 1.2000 0.90000 0.50000 -1.3000 0.20000E-01 0.0000 100.00 -100.00 0.70000 / 6533 'REECB1' W 0 0 1 0 0 -99.000 99.000 0.20000E-01 0.0000 0.0000 0.0000 1.1000 -1.1000 0.0000 0.50000E-01 0.44000 -0.44000 1.0500 0.90000 0.0000 0.10000E-01 10.000 60.000 0.20000E-01 99.000 -99.000 1.0000 0.0000 1.1100 0.20000E-01 / 6533 'REPCA1' W 0 0 0 '0 ' 0 0 1 0.20000E-01 18.000 5.0000 0.0000 0.50000E-01 0.0000 0.0000 0.0000 0.20000E-01 0.10000 -0.10000 -1.0000 1.0000 0.43000 -0.43000 1.0000 0.50000E-01 0.25000 -1.0000 1.0000 99.000 -99.000 1.0000 0.0000 0.10000 0.0000 0.0000 /

edit retag flag offensive close merge delete

Comments

Please show the data for the dynamic models (DYR records).

perolofl gravatar imageperolofl ( 2024-07-12 08:59:54 -0600 )edit

I am unable to attach data so I am sharing the link for the verified working case of WECC 240 bus system instead: https://www.nrel.gov/grid/test-case-repository.html. I used similar dynamic models for the wind generator. It would be really helpful if you can point out adjustments to this to step Q.

Stokes CB gravatar imageStokes CB ( 2024-07-12 15:22:19 -0600 )edit

Just show the data of the studied generator (REGCA1, REECB1, REPCA1).

perolofl gravatar imageperolofl ( 2024-07-12 16:25:34 -0600 )edit

I have updated my answer instead now to update sample dyr data of the models.

Stokes CB gravatar imageStokes CB ( 2024-07-13 12:00:13 -0600 )edit

Hi perolofl, any advice from your end would be really appreciated. Possibly if you could let me know which model needs to be looked into more and if using REECA1 is a better option. Thanks.

Stokes CB gravatar imageStokes CB ( 2024-07-16 03:48:33 -0600 )edit

1 answer

Sort by ยป oldest newest most voted
0

answered 2024-07-17 10:04:00 -0600

mhcastro gravatar image

Hi, Stokes CB. When I need to do this kind of event, I add a Plant Controller, for example, PLNTBU1 model. This model controls the operation mode, of a wind farm, a PV plant, or convencional plant with some generators. In the case of WF or PV, this model represent the power plant controller. With this model you will be able to make a V or Q step. First of all you have to define the kind of control your wind turbine will do, for example, V, P, Q control. Then, you can start a simulation, and then make a change at the corresponding VAR, to change, in your case, the reference of Q, Qref. That will introduce a step in Q, which is your goal.