WARNING: bus xx is not a generator bus or it is disconnected. WTG will be considered disconnected!
How to resolve this?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
How to resolve this?
Could you please check your "Code" of bus? Code=2 is generator bus, where Code=3 is swing bus of the system (also generator).
Code=1 is general bus, you can add the load on this type of bus.
Code=4 is isolated bus, which means that this bus can not be connected to swing bus.