Make Optimal Power Flow solutions more realistic
Does anyone have any tips that would help make optimal power flow produce more realistic flows and loading? How do you do a sanity check on your optimal power flow solution?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Does anyone have any tips that would help make optimal power flow produce more realistic flows and loading? How do you do a sanity check on your optimal power flow solution?
Here's my experience with OPF in PSS/E.
I was optimizing the shunt capacitor size and location. In OPF, I defined the candidate buses with base case plus contingencies. When OPF provided the shunt compensation location and size, I simulated the case with the shunt capacitor in place and applied the contingencies, if any, and see if the voltages would be at acceptable magnitudes per criteria.
This is a good check if the OPF "really" gave the optimal capacitor size and location.
amaity, I don't have a python code on this strategy...I'm sorry...usually I have an idev or python recorded but I don't have those now when I resigned from PTI...thanks.
If i dont want to use any python routine then what would be the strategy to find optiml power flow n PSSE. When I solve myt case withOPF,the solution case was blown up.
Asked: Feb 4 '12
Seen: 6,844 times
Last updated: Oct 10 '12
OPF: Unrecoverable error, solution diverging
How can I read the value worked out by OPF calcultion?
Optimal Power Flow option not installed
Is there any chance to shut down the output of OPF?
API for outputting the total cost of OPF
How to close the OPF output using API? [closed]
PSS/E OPF manual(optimal power flow)
Can i get locational marginal prices using PSS/E OPF module?