Ask Your Question
0

Kindly help to solve error in WT3P1 model. Unable to initialize

asked 2023-08-29 07:39:08 -0500

Shak gravatar image

Model WT3P1 Bus 101 [WIND] Machine "1 " : When WT operates at partial output, initial condition suspect may be reported for STATE(K+2). No action is needed

Above error was tried to solve by changing WT3E1 parameters. Kindly guide how it can be resolve....

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2023-09-01 09:01:46 -0500

perolofl gravatar image

Model WT3P1 will report initial condition suspect whenever initial generation Pgen/Mbase (pu machine base) is lower than PMX. The integrator, STATE(K+2), will be initialised to 0 while the input signal is negative. Hence, there will be initial condition suspect reported, which can be ignored.

This is not an error and it is not possible to correct it by changing WT3E1 parameters

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2023-08-29 07:39:08 -0500

Seen: 474 times

Last updated: Sep 01 '23