Ask Your Question
0

How to trip a line in power flow using pssuserpf.py?

asked 2023-06-12 07:15:53 -0600

anonymous user

Anonymous

I have a line that I monitor. During normal power flow I want to trip it if its current exceeds a certain value. RAS and pssuserpf load correctly, but when I call pfcontrol functions inside post_iteration() i receive ierr=2, which means that

not called from allowable PCI automation function

My post_iteration() funtion in pssuserpf.py looks like this:

def post_iteration():
    _, flow = psspy.brnmsc(1, 2, "1", "AMPS")
    if flow > 50.0:
        print("MUST TRIP LINE")
        ierr1 = pfcontrol.pfbrchint(1, 2, "1", "STATUS", 0)
        ierr2 = pfcontrol.pfdscnbus(2)
        print(ierr1, ierr2)
        # both ierr1 and ierr2 are always 2. 
        return False
    else:
        return True
edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2023-06-12 13:01:06 -0600

perolofl gravatar image

Use API psspy.branch_chng to trip the line and psspy.dscn to trip the bus.

edit flag offensive delete link more

Comments

As stated in POM, it is not allowed to call these functions from post_iteration(). I get: "DSCN not allowed from post_iteration power flow user exit. (006024)"

opq82047@3djahg gravatar imageopq82047@3djahg ( 2023-06-13 00:39:40 -0600 )edit

Ok, it was a long shot; I am not using RAS...

perolofl gravatar imageperolofl ( 2023-06-13 02:51:08 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2023-06-12 07:15:53 -0600

Seen: 175 times

Last updated: Jun 12 '23