It is not possible to start a generator unit during a dynamic simulation!!! All generators to be simulated must be in-service in the saved case used in the simulation so they will be initialised at start of simulation.

Synchronisation of a unit can be simulated by keeping an islanded, stand-alone AC-system with the generator bus as a swing bus and the step-up transformer switched off. The unit is then running at nominal speed until synchronisation is done by e.g. closing the step-up transformer at a proper time in the simulation.

Just be sure that the phase angle, frequence and voltage differences are sufficiently small at the instant of synchronisation.