| 1 | initial version |
I have a composite load (CMLDBLDGU2) at bus 20 for the IEEE39 network. The value of "feeder resistance =0.04" and the value of "feeder reactance = 0.04". If I run the dynamic simulation with these values, all the output is Nan.
If I change these values, for example, 2, 5, the dynamic simulation is run.
I want to run the network with the true values, (0.04, and 0.04). I have tried to shed load, but it also does not work. Could you help me with that? Thank you.
This is my .dyr file.
20, 'USRLOD', '1', 'CMLDBLDGU2', 12, 1, 8, 175, 32, 148 ,48,
0, 0 , 1 , 0, 0, 1 , 1 , 1 ,
-1 , 0.0, 0.04, 0.04, 0.08, 1.0, 1.0,
1.0, 0.9, 1.1 , 0.00625, 1.025, 1.04 , 30.0, 5.0 , 0.0, 0.0,
0.108850010868, 0.114095056656 , 0.0605301020056 , 0.0860015181818, 0.189206598581 ,
1.0 , 0.6 , 0.5 , 0.8 , 1.0,
2 , 0.647763667352 , 1 , 0.352236332648, 0.0, 2 , 1.0 , 1 , 0.0 , -1.0 ,
0.75 , 0.104 , 0.059, 0.04 ,1.8 , 0.12 , 0.095, 0.0021, 0.1 , 0.0 , 0.6 , 0.1, 0.2 ,1.0 ,99999.0 , 0.45 , 0.02 , 0.75 , 0.6 , 0.1 ,
0.75 , 0.14, 0.059, 0.03, 1.8, 0.19 , 0.2 , 0.0026 , 0.5 , 2.0 , 0.5, 0.02 ,0.3 , 0.6, 0.05, 0.45 , 0.025 ,0.3 , 0.55 ,0.05 ,
0.75 , 0.14 , 0.059, 0.03, 1.8 , 0.19 , 0.2 , 0.0026 , 0.1 , 2.0, 0.53 ,0.03, 0.2, 0.63 ,0.05, 0.48 , 0.03, 0.3, 0.58, 0.1,
0.03 , 0.3 , 0.025 , 0.05 , 1.0 , 0.98 , 0.45 , 0.1, 0.1 , 0.0 ,
0.0, 1.0 , 6.0 , 2.0, 12.0 , 3.2 , 11.0 , 2.5,
0.86 , 0.2, 0.95 , 1.0 , -3.3 , 0.5, 0.4 , 0.6, 0.5 ,
15.0 , 0.7 , 1.9 , 0.1 , 0.6 , 0.2, 0.0 , 9999.0 ,
0.0 , 0.0 , -0.1 , 0.1 , 1.0 , 0.0 , 0.025 , 0.02,
0.0, 0.0 , 0.0, 0.0, 999.0, -999.0 ,
1.1 , 0.0 , 9.0, -9., 0.1 , 0.1 , 0.05 , 1.2 ,
0.5 , 0.52 ,1.21, 1.19, 200.0 , 0.0 , 200.0, 0.0 0.5,
59.0 ,61.0 , 1.0 , 1.0, 0.02, 5.0 , 0.2 , 0.8, 0.5 , -0.5 , 0.75 , 0.5 /
30 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.30000
0.47000 0.79200E-02 0.79200E-02 0.60000E-02 0.10000 0.40000 0.10000 /
30 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.25000 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
30 'IEEEX1' 1 0.0000 10.100 0.60000E-01 0.0000
0.0000 8.0000 -8.0000 -0.50000E-01 0.25000
0.23000 1.3000 0.0000 1.7000 0.50000
3.0000 2.0000 /
30 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
31 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.30000
0.47000 0.29779 0.29779 0.15000 0.10000 0.40000 0.10000 /
31 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.25000 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
31 'IEEEX1' 1 0.0000 10.100 0.50000E-01 0.0000
0.0000 5.2000 -5.0000 -0.50000E-01 0.41000
0.23000 1.3000 0.0000 3.0000 0.66000
4.0000 0.88000 /
31 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
32 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.30000
0.47000 0.25660E-01 0.25660E-01 0.20000E-01 0.10000 0.40000 0.10000 /
32 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.40000 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
32 'IEEEX1' 1 0.0000 10.100 0.60000E-01 0.0000
0.0000 5.0000 -5.0000 -0.20000E-01 0.50000
0.23000 1.3000 0.0000 3.0000 0.13000
4.0000 0.34000 /
32 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
33 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.30000
0.47000 0.80300E-02 0.80300E-02 0.70000E-02 0.10000 0.40000 0.10000 /
33 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.20000 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
33 'IEEEX1' 1 0.0000 10.100 0.60000E-01 0.0000
0.0000 5.0000 -5.0000 -0.50000E-01 0.50000
0.23000 1.3000 0.0000 3.0000 0.80000E-01
4.0000 0.31000 /
33 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
34 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.30000
0.47000 0.57100E-02 0.57100E-02 0.40000E-02 0.10000 0.40000 0.10000 /
34 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.33300 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
34 'IEEEX1' 1 0.0000 40.000 0.20000E-01 0.0000
0.0000 9.9000 -9.9000 -0.40000E-01 0.78500
0.23000 1.3000 0.0000 3.0000 0.30000E-01
4.0000 0.91000 /
34 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
35 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.50000
0.60000 0.46538 0.46538 0.15000 0.10000 0.40000 0.10000 /
35 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.33300 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
35 'IEEEX1' 1 0.0000 10.100 0.20000E-01 0.0000
0.0000 5.0000 -5.0000 1.0000 0.47100
0.23000 1.3000 0.0000 3.0000 0.80000E-01
4.0000 0.25000 /
35 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
36 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.30000
0.47000 0.21410E-01 0.21410E-01 0.20000E-01 0.10000 0.40000 0.10000 /
36 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.20000 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
36 'IEEEX1' 1 0.0000 40.000 0.20000E-01 0.0000
0.0000 6.5000 -6.5000 1.0000 0.73000
0.23000 1.3000 0.0000 3.0000 0.30000E-01
4.0000 0.74000 /
36 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
37 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.30000
0.47000 0.60760E-01 0.60760E-01 0.50000E-01 0.10000 0.40000 0.10000 /
37 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.33300 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
37 'IEEEX1' 1 0.0000 10.100 0.20000E-01 0.0000
0.0000 5.0000 -5.0000 -0.50000E-01 0.52800
0.23000 1.3000 0.0000 3.0000 0.90000E-01
4.0000 0.28000 /
37 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
38 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.30000
0.47000 0.11740E-01 0.11740E-01 0.10000E-01 0.10000 0.40000 0.10000 /
38 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.33300 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
38 'IEEEX1' 1 0.0000 40.000 0.20000E-01 0.0000
0.0000 9.9000 -9.9000 1.0000 0.95000
0.23000 1.3000 0.0000 3.0000 0.30000E-01
4.0000 0.85000 /
38 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
39 'GENTPJ1' 1 4.8000 0.35000E-01
1.5000 0.70000E-01 3.2000 0.0000 1.8000 1.7500 0.30000
0.47000 0.26000E-02 0.26000E-02 0.20000E-02 0.10000 0.40000 0.10000 /
39 'PSS2A' 1 1 0 3 0
5 1 2.0000 2.0000 0.20000
2.0000 4.0000 2.0000 0.33300 1.0000
0.50000 0.10000 30.000 0.15000 0.30000E-01
0.15000 0.30000E-01 0.10000 -0.10000 /
39 'IEEEX1' 1 0.0000 10.100 0.20000E-01 0.0000
0.0000 9.9000 -9.9000 1.0000 0.95000
0.23000 1.3000 0.0000 3.0000 0.30000E-01
4.0000 0.85000 /
39 'IEESGO' 1 0.15000 0.0000 0.50000E-01 0.25000
4.0200 0.0000 20.000 0.60000 0.50000
0.92000 0.0000 /
whit loves you. Content on this site is licensed under a Creative Commons Attribution Share Alike 3.0 license.