Renewable generic model problem in dynamic

Hi everyone, I have initializing question about renewable in dynamic simulation.

In my case, I build a PV plant which using the machine control mode "Fixed Q based on WPF". The voltage at machine side is 0.97 p.u. under power flow solution.

In dynamic simulation, I use PVGU1 and PVEU1 as this PV plant's model. When I initialize the case, The initial condition of this machine's voltage at machine side becomes 0.79 p.u., which cause the initial condition suspect I guess.

I don't know what and why cause a such voltage deviation. Please give me some advise, thank you.

----------------------------- MACHINE INITIAL CONDITIONS -----------------------------

BUS#-SCT X-- NAME --X BASKV ID ETERM EFD POWER VARS P.F. ANGLE ID IQ

  1     PVG         23.900 1  0.7989 0.0000   46.41  -22.48 0.9000   4.13-0.2814 0.5809

INITIAL CONDITIONS SUSPECT:

  I   DSTATE(I)    STATE(I)     MODEL             STATE     BUS#-SCT X-- NAME --X BASKV  ID
4562  -0.26028E-01  0.46410     PVEU1              K+5         1     PVG         23.900  1
4564    12.135     -0.28136     PVEU1              K+7         1     PVG         23.900  1