Renewable generic model problem in dynamic

asked 2025-05-26 19:59:17 -0500

sugui_ gravatar image

Hi everyone, I have initializing question about renewable in dynamic simulation.

In my case, I build a PV plant which using the machine control mode "Fixed Q based on WPF". The voltage at machine side is 0.97 p.u. under power flow solution.

In dynamic simulation, I use PVGU1 and PVEU1 as this PV plant's model. When I initialize the case, The initial condition of this machine's voltage at machine side becomes 0.79 p.u., which cause the initial condition suspect I guess.

I don't know what and why cause a such voltage deviation. Please give me some advise, thank you.

----------------------------- MACHINE INITIAL CONDITIONS -----------------------------

BUS#-SCT X-- NAME --X BASKV ID ETERM EFD POWER VARS P.F. ANGLE ID IQ

  1     PVG         23.900 1  0.7989 0.0000   46.41  -22.48 0.9000   4.13-0.2814 0.5809

INITIAL CONDITIONS SUSPECT:

  I   DSTATE(I)    STATE(I)     MODEL             STATE     BUS#-SCT X-- NAME --X BASKV  ID
4562  -0.26028E-01  0.46410     PVEU1              K+5         1     PVG         23.900  1
4564    12.135     -0.28136     PVEU1              K+7         1     PVG         23.900  1
4566  -0.26028E-01  0.46410     PVEU1              K+9         1     PVG         23.900  1
edit retag flag offensive close merge delete

Comments

There is no message from model PVEU1 before the machine list?

perolofl gravatar imageperolofl ( 2025-05-28 01:51:08 -0500 )edit

No, there is no message show any conflict.

sugui_ gravatar imagesugui_ ( 2025-05-28 02:38:39 -0500 )edit

Is it happening during CONG process? May check ORDR, FACT, TYSL convergence. If grid is modeled as GENCLS, pl also check its parameters.

chandv gravatar imagechandv ( 2025-05-28 04:11:37 -0500 )edit

No, just some type 2 bus which has no plant and then set to 1. There is a message during TYSL, but the machine it show is far from this PV plant. By the way, my case is a complete real system, instead of a simple system, so sorry that I can not give more detail information.

sugui_ gravatar imagesugui_ ( 2025-05-28 18:09:44 -0500 )edit

I just tried a example case called "solarPV_v33", which I think it was provided by jconto before. It has the same situation that the PV plant bus 3018 voltage is 1.02 p.u. under power flow solution, and after initialize, the voltage become 0.97p.u..

sugui_ gravatar imagesugui_ ( 2025-05-28 18:31:50 -0500 )edit

1 answer

Sort by ยป oldest newest most voted
0

answered 2025-06-18 02:19:54 -0500

sugui_ gravatar image

updated 2025-06-18 02:20:31 -0500

I found that it has a large Q mismatch at bus 1 which is PV plant's generator bus. I think this is why I have a large voltage deviation. Does anyone know how would cause a large Q mismatch in initialization?

edit flag offensive delete link more

Comments

There might be a limitation of Q or reactive current in model PVEU1.

perolofl gravatar imageperolofl ( 2025-06-19 08:41:36 -0500 )edit