Renewable generic model problem in dynamic

  • retag add tags

Hi everyone, I have initializing question about renewable in dynamic simulation.

In my case, I build a PV plant which using the machine control mode "Fixed Q based on WPF". The voltage at machine side is 0.97 p.u. under power flow solution.

In dynamic simulation, I use PVGU1 and PVEU1 as this PV plant's model. When I initialize the case, The initial condition of this machine's voltage at machine side becomes 0.79 p.u., which cause the initial condition suspect I guess.

I don't know what and why cause a such voltage deviation. Please give me some advise, thank you.

----------------------------- MACHINE INITIAL CONDITIONS -----------------------------

BUS#-SCT X-- NAME --X BASKV ID ETERM EFD POWER VARS P.F. ANGLE ID IQ

  1     PVG         23.900 1  0.7989 0.0000   46.41  -22.48 0.9000   4.13-0.2814 0.5809

INITIAL CONDITIONS SUSPECT:

  I   DSTATE(I)    STATE(I)     MODEL             STATE     BUS#-SCT X-- NAME --X BASKV  ID
4562  -0.26028E-01  0.46410     PVEU1              K+5         1     PVG         23.900  1
4564    12.135     -0.28136     PVEU1              K+7         1     PVG         23.900  1
4566  -0.26028E-01  0.46410     PVEU1              K+9         1     PVG         23.900  1
Kevin Chuang's avatar
15
Kevin Chuang
asked 2025-05-26 19:59:17 -0500
edit flag offensive 0 remove flag close merge delete

Comments

There is no message from model PVEU1 before the machine list?

perolofl's avatar perolofl (2025-05-28 01:51:08 -0500) edit

No, there is no message show any conflict.

Kevin Chuang's avatar Kevin Chuang (2025-05-28 02:38:39 -0500) edit

Is it happening during CONG process? May check ORDR, FACT, TYSL convergence. If grid is modeled as GENCLS, pl also check its parameters.

chandv's avatar chandv (2025-05-28 04:11:37 -0500) edit

No, just some type 2 bus which has no plant and then set to 1. There is a message during TYSL, but the machine it show is far from this PV plant. By the way, my case is a complete real system, instead of a simple system, so sorry that I can not give more detail information.

Kevin Chuang's avatar Kevin Chuang (2025-05-28 18:09:44 -0500) edit

I just tried a example case called "solarPV_v33", which I think it was provided by jconto before. It has the same situation that the PV plant bus 3018 voltage is 1.02 p.u. under power flow solution, and after initialize, the voltage become 0.97p.u..

Kevin Chuang's avatar Kevin Chuang (2025-05-28 18:31:50 -0500) edit
add a comment see more comments

1 Answer

0

I found that it has a large Q mismatch at bus 1 which is PV plant's generator bus. I think this is why I have a large voltage deviation. Does anyone know how would cause a large Q mismatch in initialization?

Kevin Chuang's avatar
15
Kevin Chuang
answered 2025-06-18 02:19:54 -0500, updated 2025-06-18 02:20:31 -0500
edit flag offensive 0 remove flag delete link

Comments

There might be a limitation of Q or reactive current in model PVEU1.

perolofl's avatar perolofl (2025-06-19 08:41:36 -0500) edit