Hello, everyone! I'm working with a system where the governors are represented with TGOV1 model. In the PSS/E documentation it says that the droop R is given in per unit on machine base. To convert the value to the system MVA base I should use the equation:
R_system = R_machine*machineBaseMVA/systemBaseMVA
Is that correct? Thanks!