Which generators need machine dynamics?
I have a system with 20 generators. I have modeled two generators of interest but other generators are left. I can not run dynamic stability. Should I define the other generators as gencls?
add a comment
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I have a system with 20 generators. I have modeled two generators of interest but other generators are left. I can not run dynamic stability. Should I define the other generators as gencls?
Model GENCLS should only be used for equivalents and not for physical generators. Better to use e.g. GENROU or GENSAL with typical data.