Ask Your Question
0

The value of IC and IT for wind generator models

asked 2022-09-26 19:30:36 -0500

anonymous user

Anonymous

In POM.pdf, it says that "For wind machine model records (i.e., IC values of 101 through 107)..." While for wind generator models, it describes that

1.IC and IT must be specified as one.

So,whar is the value of IC for wind generator models?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2022-09-27 04:45:28 -0500

perolofl gravatar image

It is a copy and paste error in the manual. IC must be 101 and IT must be 1.

edit flag offensive delete link more

Comments

Thanks, but I have never succeeded with 'ENTRY' point in current injection model, the voltage of that bus became very small and I don't know how to solve this problem.

dat gravatar imagedat ( 2022-09-27 18:48:02 -0500 )edit

It is very advanced to write ypur own generator model!

perolofl gravatar imageperolofl ( 2022-09-28 04:33:03 -0500 )edit

I agree, so there is not a simple example for user-written generator model and we have to figure it out ourselves? I know there is 'write a basic load model' in POM.pdf, but It doesn't seem to work for me.

dat gravatar imagedat ( 2022-09-28 19:05:37 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2022-09-26 19:30:36 -0500

Seen: 114 times

Last updated: Sep 27 '22