Ask Your Question
0

Reactive control loop REPC

asked 2022-08-19 04:19:59 -0500

pff gravatar image

In the REPCA model for reactive control the deadband is defined using dbd1, lower threshold for reactive power control deadband (<=0) and dbd2, upper threshold for reactive power control deadband (>=0). Nevertheless, there are two CONs I can't understand, emax and emin ( upper/lower limit on deadband output (pu)). If you have a deadband of +/-0,01pu at field, are dbd1=-0.01 and dbd2=0.01? And emax/emin?

Thanks ina dvance

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2022-08-20 04:53:26 -0500

perolofl gravatar image

Constants emax and emin are just limitations on the input signal to the PI Q-controller. Enter large positive and negative numbers to ignore the limitation.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2022-08-19 04:19:59 -0500

Seen: 239 times

Last updated: Aug 20 '22