Ask Your Question
0

Synchronous Generator Controllers

asked 2021-12-12 09:42:22 -0500

Muhammad Sarim gravatar image

I have a question regarding the IEEE-09 Bus system. There are three generators of which Gen1 is swing generator. Its controller is GENSAL while others two have GENROU controllers. Is there any logic behind this type of sequence. Please refer any research paper or website which have regarded this sequence.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-12-13 02:22:44 -0500

perolofl gravatar image

Generally speaking, model GENROU is used for solid rotor generators (e.g. thermal power) and model GENSAL for salient pole generators (e.g. hydro power). Read Chapter 15 in Program Application Guide, Volume 2!

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

Stats

Asked: 2021-12-12 09:42:22 -0500

Seen: 290 times

Last updated: Dec 13 '21