How to add circuit breaker at each end of transmission line?

asked 2021-12-06 03:00:10 -0600

Awab Alameen gravatar image

For voltage control we need to open transmission line from one end

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-12-06 03:23:05 -0600

perolofl gravatar image

The classical way is to split the bus and move the branch to the new bus and open the zero impedance line inserted between the two buses.

edit flag offensive delete link more

Comments

Thanks very much.

Awab Alameen gravatar imageAwab Alameen ( 2024-03-16 05:03:57 -0600 )edit