Ask Your Question
0

How to add circuit breaker at each end of transmission line?

asked 2021-12-06 03:00:10 -0500

Awab Alameen gravatar image

For voltage control we need to open transmission line from one end

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-12-06 03:23:05 -0500

perolofl gravatar image

The classical way is to split the bus and move the branch to the new bus and open the zero impedance line inserted between the two buses.

edit flag offensive delete link more

Comments

Thanks very much.

Awab Alameen gravatar imageAwab Alameen ( 2024-03-16 05:03:57 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2021-12-06 03:00:10 -0500

Seen: 199 times

Last updated: Dec 06 '21