Ask Your Question
0

WECC generic models tunable parameters

asked 2021-10-14 01:21:41 -0500

pff gravatar image

When you compare tests measurements to simulations using WECC models (i.e. REECA and REPCA models), the parameters you should modify are:

REECB REPCA Tunable Parameters pfflag |vflag |qflag ||refflag ||Local || Plant 0 |0 | 0 || 0 || Kqv || Kp, Ki 0 |0 | 0 || 1 || Kqv || Kp, Ki 0 |0 | 1 || 0 || Kqv,Kvp,Kvi || Kp, Ki 0 |0 | 1 || 1 || Kqv,Kvp,Kvi || Kp, Ki 0 |1 | 0 || 0 || Kqv || Kp, Ki 0 |1 | 0 || 1 || Kqv || Kp, Ki 0 |1 | 1 || 0 || Kqv,Kqp,Kqi,Kvp,Kvi || Kp, Ki 0 |1 | 1 || 1 || Kqv,Kqp,Kqi,Kvp,Kvi || Kp, Ki

Normally, in the studies I have seen only plant parameters are modified. The local parameters are the ones the manufacturer gives or should they be modified too?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-10-14 03:23:24 -0500

lmcqueen gravatar image

If you are simulating a manufacturer-specific inverter, you cannot proceed to tune these parameters without consulting them. Typically, generic dynamic models from inverter manufacturers have these parameters already configured; you may need to update Project-specific settings such as Pmax, Pmin, Qmax, Qmin.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2021-10-14 01:21:41 -0500

Seen: 297 times

Last updated: Oct 14 '21