WECC generic models tunable parameters

asked Oct 14 '1

pff gravatar image

When you compare tests measurements to simulations using WECC models (i.e. REECA and REPCA models), the parameters you should modify are:

REECB REPCA Tunable Parameters pfflag |vflag |qflag ||refflag ||Local || Plant 0 |0 | 0 || 0 || Kqv || Kp, Ki 0 |0 | 0 || 1 || Kqv || Kp, Ki 0 |0 | 1 || 0 || Kqv,Kvp,Kvi || Kp, Ki 0 |0 | 1 || 1 || Kqv,Kvp,Kvi || Kp, Ki 0 |1 | 0 || 0 || Kqv || Kp, Ki 0 |1 | 0 || 1 || Kqv || Kp, Ki 0 |1 | 1 || 0 || Kqv,Kqp,Kqi,Kvp,Kvi || Kp, Ki 0 |1 | 1 || 1 || Kqv,Kqp,Kqi,Kvp,Kvi || Kp, Ki

Normally, in the studies I have seen only plant parameters are modified. The local parameters are the ones the manufacturer gives or should they be modified too?

1 answer

Sort by » oldest newest most voted
0

answered Oct 14 '1

lmcqueen gravatar image

If you are simulating a manufacturer-specific inverter, you cannot proceed to tune these parameters without consulting them. Typically, generic dynamic models from inverter manufacturers have these parameters already configured; you may need to update Project-specific settings such as Pmax, Pmin, Qmax, Qmin.