Ask Your Question
0

Fault current calculation in PSSEv34

asked 2021-10-03 23:45:23 -0500

sugui_ gravatar image

In PSSEv34 or higher version, we can add distributed generation data in load. In fact, inverter-based generation resources will still contribute fault current although they connect to grid through power electronic components.

My question is, if I build a distributed generation resource in load data, does the fault current calculation of PSSE take this part into consideration? Thank you.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-10-05 03:46:35 -0500

perolofl gravatar image

No, the distributed generation is not modelled as generation in short circuit calculation or in dynamic simulation.

The effective load is the normal load netted with the distributed generation.

edit flag offensive delete link more

Comments

Thanks for your answer. It will be a little annoying that if I want to take distributed generation's effect into consideration in fault current calculation, I have to build a machine data. Thus, I'm wondering if this function can simply my case, and I didn't find the relevant information neither.

sugui_ gravatar imagesugui_ ( 2021-10-05 18:39:34 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2021-10-03 23:45:23 -0500

Seen: 301 times

Last updated: Oct 05 '21