Ask Your Question
0

TIOCR1 Rely modelling

asked 2021-08-18 12:17:55 -0500

chandan kuamr gravatar image

PSSE has one Relay model called TICOR1 for overcurrent relay-based tripping and load shedding in their model list.

I would like to use this feature for overload-based tripping feature during dynamic for branches (Lines/ICTs).

I want to model the following

400 kV Line A-B circuit 1 is to be monitored for overloading

Logic is if its loading exceeds 2500 Amps (10 pu on 100 MVA Base) for 5 seconds (definite time, 250 cycles) then 50 % trip load connected from Bus A and trip this line and parallel circuit 2 immediately.

How to implement the same through this relay.

We could not find any explanation and how to implement a definite time feature through this line relay.

Can someone explain to me how to set up.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-08-19 03:13:03 -0500

perolofl gravatar image

Model TIOCR1 is a time inverse relay. You want to use it with definite time of 5 s. See description in manual Program Application Guide, vol II, Chapter 20.9.

Try with same multiple (1 pu of threshold current) for all four current points defining the time inverse curve. Use 5 s for all relay closing times.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2021-08-18 12:17:55 -0500

Seen: 366 times

Last updated: Aug 19 '21