Ask Your Question
0

HVDC Power Oscillation Damping Test model

asked 2020-12-14 19:57:19 -0600

Song gravatar image

Hi, I have been worked in Power Utility

LCC HVDC project are on going and we received the PSS/E UDM model from GE It has Power Oscillation Damping controller in PSS/E model, and we want to test its function whether it works well or not However, It is difficult to make its phenomenon artificially(power oscillation)

Is there any dynamic model to inject or generate power oscillation artificially??

Thank ou

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-12-18 08:44:35 -0600

jfconroy gravatar image

GE should have provided a "power oscillation damping tuning" report, perhaps with a different name, but the report should show how they calculated the controller parameters for their power oscillation damper (POD). To test the POD in PSS/E, you should have a dynamic model of your entire network, with the GE HVDC model included. Then, to initiate oscillations, you can implement simulation events such as faults, generator trips, load trips, capacitor bank trips etc. You should do these simulations with and without the POD activated, to see how the POD decreases/increases the size (magnitude and damping) of any oscillations. If the POD is decreasing the size of the oscillations, then it is doing its job correctly. If the POD is causing the oscillations to be larger, then its tuning needs to be adjusted.

Alternatively, you could do a small-signal analysis (eigenvalue) comparison with and without the POD using the add-on module NEVA for eigenvalue analysis, but maybe you do not have this add-on module.

edit flag offensive delete link more