4 winding transformer
Hi, i need suggestion , how to model 4 winding transformer in PSSE. i have 345 kV high side and two 34.5 kV low of transformer, If i use 3 winding model than how can i control two low voltage winding with OLTC?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Hi, i need suggestion , how to model 4 winding transformer in PSSE. i have 345 kV high side and two 34.5 kV low of transformer, If i use 3 winding model than how can i control two low voltage winding with OLTC?
Practically, if you are regulating the voltage at one of the low voltage winding, the tap at HV get adjusted and the other Low voltage winding voltage will also get adjusted automatically.
You can have tap changer control on both low voltage windings.