Ask Your Question
0

4 winding transformer

asked 2020-11-19 15:57:20 -0500

anonymous user

Anonymous

Hi, i need suggestion , how to model 4 winding transformer in PSSE. i have 345 kV high side and two 34.5 kV low of transformer, If i use 3 winding model than how can i control two low voltage winding with OLTC?

edit retag flag offensive close merge delete

2 answers

Sort by ยป oldest newest most voted
0

answered 2020-11-21 06:26:21 -0500

Practically, if you are regulating the voltage at one of the low voltage winding, the tap at HV get adjusted and the other Low voltage winding voltage will also get adjusted automatically.

edit flag offensive delete link more
0

answered 2020-11-20 02:10:53 -0500

perolofl gravatar image

You can have tap changer control on both low voltage windings.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2020-11-19 15:57:20 -0500

Seen: 469 times

Last updated: Nov 21 '20