First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!

Ask Your Question
0

machine modeling in steady state for solar inverter

asked Oct 10 '0

Vikas07 gravatar image

In PSSE, while modeling solar inverter as a machine for steady state. How do you define the parameters like X source , Subtransient,Transient,Synchronius, Zero and Negative impedance while modeling ? What values to be considered ? Thanks in Advance

2 answers

Sort by » oldest newest most voted
0

answered Oct 10 '0

Based the fault current contribution from Inverter (typically 1.1 times the inverter rated current), the Impedance can be calculated and parameters like X source , Sub transient, Transient, Synchronous reactance shall be kept Identical in this case.

link

Comments

Thanks for the reply. I know the maximum converter current limit of the inverter. Eg. 1.068 pu. Can i define all the impedance parameters as 1/1.068 = 0.9363 pu ?

Vikas07 gravatar imageVikas07 (Oct 10 '0)

Yes, exactly. You can use the same parameters for PV inverter in the steady state model.

Berwin gravatar imageBerwin (Oct 11 '0)
0

answered Oct 10 '0

lmcqueen gravatar image

Xsource is usually set at a very large value e.g. 9999 p.u. However, please note that manufacturer's data of inverter shall be consulted before doing the modeling work. They typically provide modeling procedure of inverter for PSS/E steady-state and dynamic studies. An Aspen Oneliner modeling note is also given for short-circuit studies as well.

link

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.
Want to format code in your answer? Here is a one minute demo on Youtube

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: Oct 10 '0

Seen: 1,121 times

Last updated: Oct 10 '20