Network sequence reduction

asked 2020-09-03 20:37:06 -0600

cheema gravatar image

I'm working on a substation which has four transmission lines coming into it. I have the full grid model with around 2400 buses. Is there anyway in PSSe to get the thevenin equivalent of the four remote buses to my station? I want to model my station only with the 4 remote buses Thevenin Equivalent and the respective 4 lines.

edit retag flag offensive close merge delete

Comments

Modeling individual remote buses may be a challenge because it is highly likely that these 4 remote buses contain common connections some buses away from it. If the 4 transmission lines are radial and lead to individual network, then your objective can be achieved by applying EEQV to each network.

lmcqueen gravatar imagelmcqueen ( 2020-09-03 22:44:16 -0600 )edit

Yes, those remote buses are tied to each other through multiple routes and a part of a big grid. So it won't likely be a straightforward seperate Thevenin Equivalent for each bus.

cheema gravatar imagecheema ( 2020-09-04 09:43:10 -0600 )edit

Then you may have to represent the four remote buses to single equivalent network while maintaining four transmission lines.

lmcqueen gravatar imagelmcqueen ( 2020-09-04 10:24:07 -0600 )edit