Can someone confirm if the 2nd Generation Renewable Models (i.e. the REECAU1/REECBU1/REECCU1) has momentary cessation capability? Thank you.

1 answer

Sort by » oldest newest most voted
0

answered Aug 23 '0

oppossumX gravatar image

In short, yes. The REECBU1 model is not allowed by some ISO's because it does not have the "VDL" logic described below.

The REECAU1 and REECCU1 models have the "VDL" V-I characteristic curve parameters that define the momentary cessation characteristics. At VDL voltages V1 to V4 the corresponding limits for the active and reactive current commands Ip and Iq are defined. This enables the model to reduce or completely stop producing active and/or reactive power when low voltages are observed and then ramp back up once voltages increase.

There are other parameters in the models that can impact this behavior. The REGCAU1 model includes an ICON for LVPL switch that enables the LVPL characteristic that can also define reduction in active power at low voltages, however, this characteristic is a single, linear-slope while the VDL logic is piece-wise linear.

link

Comments

Thank you. Yes you are right. After doing research, I found a certain document from Sandia describing the parameters that influence momentary cessation.

lmcqueen gravatar imagelmcqueen (Aug 23 '0)

Hi ffl, would you mind providing a link to the document you are referring to?

ddhungana gravatar imageddhungana (Aug 24 '0)