Momentary Cessation Capability in 2nd Gen Renewable Models
Can someone confirm if the 2nd Generation Renewable Models (i.e. the REECAU1/REECBU1/REECCU1) has momentary cessation capability? Thank you.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Can someone confirm if the 2nd Generation Renewable Models (i.e. the REECAU1/REECBU1/REECCU1) has momentary cessation capability? Thank you.
In short, yes. The REECBU1 model is not allowed by some ISO's because it does not have the "VDL" logic described below.
The REECAU1 and REECCU1 models have the "VDL" V-I characteristic curve parameters that define the momentary cessation characteristics. At VDL voltages V1 to V4 the corresponding limits for the active and reactive current commands Ip and Iq are defined. This enables the model to reduce or completely stop producing active and/or reactive power when low voltages are observed and then ramp back up once voltages increase.
There are other parameters in the models that can impact this behavior. The REGCAU1 model includes an ICON for LVPL switch that enables the LVPL characteristic that can also define reduction in active power at low voltages, however, this characteristic is a single, linear-slope while the VDL logic is piece-wise linear.
Asked: 2020-08-19 07:05:01 -0500
Seen: 491 times
Last updated: Aug 22 '20
What is the base value used for the PMAX and PMIN values in REECB1 and REPCA1
How to simulate reduced system inertia while integrating renewables?
renewable generation not shown in load flow
How do I model a wind turbine to study its fault current contribution?
Mathematical Expressions of Generic Renewable Models
Question about coordinated call models
Help with User written model for FACTS devices