Short circuit equivalent generator

asked 2020-05-28 05:45:36 -0500

Vikas07 gravatar image

A couple of questions on modelling short and equivalent generator for short circuit analysis. 1) How to derive the max short circuit MVA at a bus. 2) The Zth is available , but how to get X0/X1 ratio for representing zero and positive seq reactance in SC paramter of generator. Thanks in Advance

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-06-01 08:08:16 -0500

GaryB gravatar image

You should know at a minimum the system contribution to three-phase faults (magnitude and angle) and line-to-ground faults. With these, you can use what's in a power system analysis book to derive what you need. You also should consider transient and sub-transient responses and some way to optimize other model parameters to reflect that of the system you're modelling.