I have a two machine system consisting of a grid forming inverter and an equivalent generator representing the grid. There is an inverter step-up transformer, collector line, a main transformer and a line connecting to the equivalent generator as POI. I would appreciate if you could provide me a typical sequence for black start studies. Thank you.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-06-03 03:12:34 -0500

jfconroy gravatar image

What is the intention of your studies? Do you want to do power flow analysis, or analyse transients? I suspect that PSS/E is not the correct simulation tool for you to use.

edit flag offensive delete link more

Comments

That is what I'm actually thinking. The study is a requirement by the utility and should be done using PSS/E and PSCAD.

lmcqueen gravatar imagelmcqueen ( 2020-06-07 21:15:57 -0500 )edit

With PSS/E you will get power flow and transient stability results. When you're analysing a black start scenario, you also want to know about phenomena like transformer inrush, line and cable energization etc. For those you will need PSCAD or EMTP.

jfconroy gravatar imagejfconroy ( 2020-06-08 06:31:47 -0500 )edit

The goal of the study is to evaluate the inverter response when operating as a grid forming mode. Black start is one of the tests to evaluate its response.

lmcqueen gravatar imagelmcqueen ( 2020-06-12 06:33:22 -0500 )edit