To understand for LCFB1 model
Hello, I am currently styding on LCFB1 model. I want to know, Is the Pmwset equal to Pref0? If not, what is Pref0?
If I want to change the setpoint power of generator, should I change to pref0 through VAR(L+2)?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Hello, I am currently styding on LCFB1 model. I want to know, Is the Pmwset equal to Pref0? If not, what is Pref0?
If I want to change the setpoint power of generator, should I change to pref0 through VAR(L+2)?
Model LCFB1 is an AGC model, i.e. for automatic secondary frequency control of a generator, for example to restore the frequency back to nominal (50/60 Hz).
Model LCFB1 is not needed if you want to manually change the power setpoint for a governor model , just update GREF for the governor model.
Finally, Pmwset is not equal to Pref0.