Ask Your Question
0

Equivalent circuit: Represent external grid

asked 2019-08-15 04:39:20 -0500

Dyn_Danmark gravatar image

Hi,

I have got SCC = 19000 MVA, I3F=34 kA and XO/X1=0.8 from a DSO. How to I calculate Impedances (R and X values) and set up the generator in PSS/E?

edit retag flag offensive close merge delete

Comments

I would calculate this as follows: Xth = X1 = MVAbase/MVAsc = 100/19000 = 0.00526 p.u. X0 = 0.8X1 = 0.8(0.00526) = 0.004208 p.u. Now, Xsorce = 0.00526 X0 = 0.004208

ffl gravatar imageffl ( 2019-08-19 00:53:25 -0500 )edit

1 answer

Sort by » oldest newest most voted
0

answered 2019-08-16 03:19:55 -0500

perolofl gravatar image

Enter a generator with MBASE=19000, XSORCE=1 and Zero-X=0.8. The other short circuit reactances shall remain their default value, 1 pu. This generator will supply 19000 MVA short circuit power.

The bus base voltage must be 322.6 kV in order to get a three phase fault current of 34 kA. 322.6kV * 34kA * 1.73 = 19000 MVA!

edit flag offensive delete link more

Comments

@perolofl Your information was very useful, in the case of using GENCLS what values ​​would be in Rsource and P, P max and Pmin, in addition to Q, Qmax and Qmin. Thanks for your help

Cris_Mx gravatar imageCris_Mx ( 2021-09-29 13:04:26 -0500 )edit

Set Rsource to the wanted R/X ratio of the short circuit power. Set Pgen and Vscheduled to the wanted power and voltage at bus. An alternative is to fix Q by setting Qmax=Qmin.

perolofl gravatar imageperolofl ( 2021-09-30 00:55:53 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

2 followers

Stats

Asked: 2019-08-15 04:39:20 -0500

Seen: 824 times

Last updated: Aug 16 '19