Equivalent circuit: Represent external grid
Hi,
I have got SCC = 19000 MVA, I3F=34 kA and XO/X1=0.8 from a DSO. How to I calculate Impedances (R and X values) and set up the generator in PSS/E?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Hi,
I have got SCC = 19000 MVA, I3F=34 kA and XO/X1=0.8 from a DSO. How to I calculate Impedances (R and X values) and set up the generator in PSS/E?
Enter a generator with MBASE=19000, XSORCE=1 and Zero-X=0.8. The other short circuit reactances shall remain their default value, 1 pu. This generator will supply 19000 MVA short circuit power.
The bus base voltage must be 322.6 kV in order to get a three phase fault current of 34 kA. 322.6kV * 34kA * 1.73 = 19000 MVA!
Asked: 2019-08-15 04:39:20 -0600
Seen: 1,072 times
Last updated: Aug 16 '19
I would calculate this as follows: Xth = X1 = MVAbase/MVAsc = 100/19000 = 0.00526 p.u. X0 = 0.8X1 = 0.8(0.00526) = 0.004208 p.u. Now, Xsorce = 0.00526 X0 = 0.004208