I created the SLD with having buses and lines. I am having the settings in diagram as 'bind changes to network data'. suddenly PSSE stopped working. I could not save the file. When I again open the auto recovered version, I can see that there is a data in .sav file but .sld file shows the pink SLD. and dialogue box does not open for those unsaved lines and buses. How can I see the dialogue box . Please help. thanks.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2019-05-01 16:10:11 -0500

jconto gravatar image

The 'pink' sld is shown when values (like voltages or flows) in the sld are not know. Solve the powerflow to update those values.
New network elements added would be in pink (or not represented) until values and topology issues are resolved.

edit flag offensive delete link more

Comments

Pink objects means topology error, i.e. the object does not exist in the network. Solving the load flow will not help since the object is missing. Unsolved network is indicated with dimmed values.

perolofl gravatar imageperolofl ( 2019-05-02 00:45:55 -0500 )edit