How to set Induction motor load model parameters in PSS/E 33?

asked Jan 2 '19

psseboy gravatar image

I'm researching on Voltage Stability of Induction Motor Load Model in PSS/E 33, but there any guide to set parameters ,who can help me ?

Comments

First, look at the documentation PAGV2.pdf to check load models. There is a suggested induction motor model to be used. If you're going to study an actual motor, get its manufacturer's data (e.g. Locked Rotor Current/Torque, Breakdown, Starting P.F.).

lmcqueen gravatar imagelmcqueen (Jan 9 '19)

After getting the data, enter those in the IMD33 program inside the installation folder. The program estimates the equivalent circuit parameters of induction motor from nameplate/manufacturer's data. Use the IMD33 program to generate the *.dyr file for the motor dynamic model.

lmcqueen gravatar imagelmcqueen (Jan 9 '19)