Hi guys, I am trying to establish a circuit equivalent of a part of big power system. I used the PSSE toolbox for that and it also showed the message that the equivalence process is done, however, I was not able to see (or at least extract) the generated equivalent data. Can you help me on this issue? I would appreciate any kind response to this. Thanks,

edit retag flag offensive close merge delete

Comments

What commands did you use to create the equivalence?

JervisW gravatar imageJervisW ( 2012-10-02 05:50:26 -0500 )edit

2 answers

Sort by ยป oldest newest most voted
1

answered 2012-10-18 11:43:57 -0500

EBC gravatar image

Hi Pooya, if ever you have not find an answer to your question, I will try here...

Create a sld of the part of the big power system you are establishing a circuit equivalent including the BUS (PSS/E calls this boundary bus) where you will assign the equivalent model. Then go through equivalencing (BGEN/EEQV or whatever), when you finish the procedure, the sld is revised to reflect your equivalent. There you will be able to see your generated equivalent data.

edit flag offensive delete link more
0

answered 2017-08-23 21:08:20 -0500

Gary22212 gravatar image

Hi, You can just save the raw file (power flow raw data) and note that do not check the "output bus names", then you can get the equivalent data.