Ask Your Question
0

Rectifier no longer controlling the order?

asked 2018-07-31 15:12:51 -0500

MRS2016 gravatar image

Hi everyone,

I've run into this error below when trying to perform a dynamic study, and I'm not sure as to what this means or how to fix it.

AT TIME =10.0000 TWO-TERMINAL DC LINE "LINE_1" RECTIFIER NO LONGER CONTROLLING THE ORDER

AT TIME =10.0000 TWO-TERMINAL DC LINE "LINE_2" RECTIFIER NO LONGER CONTROLLING THE ORDER FLOW1 BUS 0 NOT FOUND--CIRCUIT 0 FROM 0 TO 0 NO SMF INPUT SIGNAL FOR CHSVCT AT BUS 16020 [AREA 1 15.000] FLOW1 BUS 0 NOT FOUND--CIRCUIT 0 FROM 0 TO 0 NO SMF INPUT SIGNAL FOR CHSVCT AT BUS 17054 [AREA 2 15.000]

Has anyone come across this issue before and if so, could you please inform me on how to fix it.

Thank you.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2018-07-31 17:28:17 -0500

MRS2016 gravatar image

Nevermind, fixed it by decreasing the additional load size, along with changing the order to assume all branches are in service and the switching studies TYSL to flat start

edit flag offensive delete link more

Comments

Hi MRS2016, I would like to reach you on email to discuss my work on two-terminal dc line.

cresg gravatar imagecresg ( 2020-08-18 09:08:39 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2018-07-31 15:12:51 -0500

Seen: 457 times

Last updated: Jul 31 '18