Dynamic Simulation Flow

Hi,

I am new to PSSE and I am unsure what the error message below means.

2455 diagonal and 3512 off-diagonal elements FLOW1 BUS 0 NOT FOUND--CIRCUIT 0 FROM 0 TO 0 NO SMF INPUT SIGNAL FOR CHSVCT AT BUS 16020 [HIGH LV6 15.000] FLOW1 BUS 0 NOT FOUND--CIRCUIT 0 FROM 0 TO 0 NO SMF INPUT SIGNAL FOR CHSVCT AT BUS 17054 [ARCENC2 15.000]

MRS2016's avatar
1
MRS2016
asked 2018-04-25 12:12:32 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

There are two switched shunts at buses 16020 and 17054 using dynamics model CHSVCT. It seems like the supplemental modulation function (SMF) is activated with ICON(I+1), but there is no branch defined in ICON(I+2) to ICON(I+4).

The error message is harmless, it just informs that the SDM control is not active. Try to change ICON(I+1) to 0 to disable the control.

perolofl's avatar
3.8k
perolofl
answered 2018-04-25 16:25:12 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you for the advice, it makes sense as all the values for ICON except the 'External bus number of remotely regulated bus' is 0. Though ICON(I+1) is already 0 when this error occurs, so I am not sure what to do from there.