Ask Your Question
0

parameters of governor model

asked 2017-09-18 20:48:19 -0500

anonymous user

Anonymous

What is U0 and Uc in IEEEG1 model?

As far as I know, they are valve velocity [p.u./sec], right? And I want to know whether they are similar to ramp rate of generator or not. Also are they based on Machine (p.u. is based on MVA?) or frequency (p.u. is based on Hz??)

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2017-09-19 00:05:50 -0500

perolofl gravatar image

Yes, they are maximum valve velocity for opening and closing respectively. They are thereby limiting how fast the turbine power may change at frequency deviations and are based on pu Mbase, i.e. maximum ramp rate. All signals after the first leadlag block are in pu power. The sum of parameters K1 - K8 should be 1.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2017-09-18 20:48:19 -0500

Seen: 6,348 times

Last updated: Sep 19 '17