Bus number too long, workaround
I am importing case data from Aspen OneLiner to PSSE, and due to an old numbering scheme some buses have 7 digit numbers. Is there a setting to ignore the 7th digit of these numbers or do I have to modify all of them?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I am importing case data from Aspen OneLiner to PSSE, and due to an old numbering scheme some buses have 7 digit numbers. Is there a setting to ignore the 7th digit of these numbers or do I have to modify all of them?
I tried to create some 7 digit numbers, looks like you're limited to 6 digits. You can use commenting to make a "memo" field in raw files to preserve a lookup to your original 7 digit numbers if you want to do that. Here's an example of what I do:
1234 'bus name ' 138.00 1 1 1 1 1.0247 2.435 /* [bus name ] */